Do you have an answer to this? Same warning here! br Chris
|
6/5/2014 10:06 AM | |
Joined: 3/20/2013 Last visit: 4/3/2024 Posts: 676 Rating: (44) |
I got an answer :) In TIA you see the language option beyond the properties of the OPC server at "S7". There is sth called "OPC messages" where you can choose the language. (see Screen_1) In STEP 7 V5.5 it is a bit more difficult. These are the steps to get rid of the Warning "No language was selected for the alarm text language): 1. Go to Netpro 2. Go inside the properties of an S7-connection 3. Go to tab OPC and choose in Connection establishment "the connection remains permanently established" (after the steps you can go back to the required connection establishment) 5. Choose Message text details and choose there your language 6. Save &Compile Have a look at the Scrennshots. Screen_2- Screen_4 are for STEP 7 V5.5. AttachmentScreenshots.zip (313 Downloads) |