I write here for the first time because I'm facing the environment simatic only now, but let's get to my problem:I want to control a logo! OBA7 (with ethernet) advanced from WinCC flexible 2008 (PC Runtime). I followed various guides but the end result is always this: "collegamento Interrotto" (the phrase is in Italian but I think it translates into "broken link"). In attachment I put the screen of the error and the configuration pages of logo! and of wincc.
Thanks in advance for your help! AttachmentWInCC problem.zip (426 Downloads) |
9/8/2014 8:11 AM | |
Posts: 2930 Rating: (432)
|
Hi, use the S7-200 driver in WinCC flex 2008. At this time LOGO! was not included in WinCC flex. But LOGO! 7 acts as a S7-200. To get FB parameters from LOGO! to WinCC use the VM-Mapping table in LOGO!, select the FB and the parameter. You get a V-Memory adress. This adress you can use in WinCC flex. Observe LOGO! only has DB1. You can also have a look to the LOGO! internet pages and the published examples for LOGO! 7. Here you find an example of how to use LOGO! 7 together with WinCC Flex. But it is based on a newer version of WinCC flex. LOGO! Internet Page Hope this helps |