S7-200 plc is password protected, we know the password but at the time of upload it doesn't ask for password it shows error message " The Plc has been protected to prevent program upload". What is the procedure to upload program, and where we can inset password to upload program. We does not have Original backup .
---------------------------------------------------------------------------------------------------- |
Last edited by: Min_Moderator at: 3/24/2015 11:29:27 AMNew subject after splitting |
|
3/25/2015 8:23 AM | |
Joined: 5/28/2008 Last visit: 9/21/2024 Posts: 4515 Rating: (839)
|
Hello, If you are the programmer, Then you should have a backup of PLC program. If not, I am sorry to tell that you won't be able to modify anything in the CPU! The only possibility is to reset the CPU to factory setting and reprogram it. S7-200 has 4 protection levels as per the attached picture. For Level 4, you can not upload the program even if you know the password. To reset the CPU to factory setting, Please use WIPEOUT tool and please note that if you used WIPEOUT tool, you will lose user program, data blocks and all confugration settings. Resetting the S7-200 to the factory default settings (WIPEOUT) |