Dear Sir, You could use a lot of SFC or SFB blocs for read or write information to a DP slave. To deactivate / activate a DP slave you have the SFC 12 " D_ACT_DP" To read/write function, you have the SFC 58, 59 and SFB 53, 54 . With help of this function blocs, you could read the parameter: SP_D ( setpoint of bloc) and with bit 0 in byte 1, you could activate/deactivate Autocal ( byte 1 = digital/ analog value, Byte 2 = status.) If you have install the EDD for Ultramat with Simatic PDM, you find more information concerning all parameters you could have access with Profibus, but you could also upload the manual from the support home page: http://support.automation.siemens.com/WW/view/en/10807005/133300 |
2/28/2008 1:16 PM | |
Posts: 4 Rating: (0) |
Dear Tribute, Thank you very much for your precious help! But "bit 0 in byte 1": is it correct? I understood from manual I need to send "1" to bit1 in byte1 to cancel autocal. Best Regards Victor |