Hello tekisyen_sistem; There are no Modbus TCP blocks available from Siemens for the S7-200. One possible solution: You could purchase the Modbus RTU library for MicroWin and then use a gateway from Modbus TCP to Modbus RTU to connect with your Schneider PLC. See here for Modbus RTU instructions: How do you implement MODBUS communication with S7-200? Hope this helps, Daniel Chartier |