4/10/2008 4:19 PM | |
Joined: 1/4/2007 Last visit: 10/15/2024 Posts: 1147 Rating: (175) |
Dear Sebastian_NLS The Lifebit-Error is active, if there is no communication between the Siwarex MS module and the S7-200 PLC. Every 500ms, the communication is checked from the library "MicroScale" into the S7-200 pogram. If the Siwarex MS module is not answering during these 500ms, the Lifebit-Error appears. You must control the parameters “First_AEW”, “Second_AEW”, “Third_AEW”, Fourth_AEW”, “First_AAW”, “Second_AAW”, “Third_AAW” and Fourth_AEW” of the library: These parameters must have thecorrect periphery-addresses from the Siware MS module. Please see also the attached file. Best regards AttachmentSiwarex_MS.pdf (539 Downloads) |
4/11/2008 11:14 AM | |
Joined: 1/4/2007 Last visit: 10/15/2024 Posts: 1147 Rating: (175) |
Dear Sebastian_NLS, Another reason can be, that you didn’t deactivate the Analog Input filters from the Analog Input addresses, which the Siwarex MS is using. This is very important! You can find an abridgement from the Siwarex MS manual into my reply. There you can find into the chapter 8.2 how to deactivate the Analog Input filters. You can find the whole manual into the internet at the address: http://support.automation.siemens.com/WW/view/en/22408486/133300 There exist no reset or acknowledge bit for reset the lifebit-error. The lifebit-error disappears automatically, if the communication between the library and the Siwarex MS module is working. Best regards AttachmentStep7.pdf (498 Downloads) |
4/11/2008 1:27 PM | |
Posts: 32 Rating: (0) |
Hello, the filter analog input is disabled, i read the manual and follow the steps. Best regards, when works the program i post the solution. |