5/14/2012 10:00 AM | |
Posts: 319 Rating: (9) |
We are using library files and we have tried odd, even and no parity. And in all configurations we got the message as request timed out. |
5/15/2012 7:25 AM | |
Posts: 319 Rating: (9) |
Sure u can have it.
AttachmentSlave Modbus.zip (431 Downloads) |
5/16/2012 7:44 PM | |
Posts: 559 Rating: (87) |
Dear nandgate, I have checked your backup & corrected it. Kindly check that backup & revert back to me. There was only problem of SM0.0 used for MODBUS_INIT. This block should be called for first scan only. AttachmentSlave Modbus.zip (479 Downloads) |
This contribution was helpful to2 thankful Users |
5/17/2012 3:13 PM | |
Posts: 319 Rating: (9) |
Thank you guys. This thing is working now. |
5/21/2012 7:00 PM | |
Posts: 153 Rating: (2) |
good job SolutionFinder!!!! keep it up |
This contribution was helpful to1 thankful Users |
4/7/2014 1:12 PM | |
Joined: 9/1/2005 Last visit: 10/14/2024 Posts: 4109 Rating: (195) |
follow up question published bygirish bodhaleis split to a seperate thread with the subjectModscan - details of converter cable. Best regards CS Moderator |
My Forum is the place to personalize your profile, |
|
4/3/2017 4:12 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by 12hemang is split to a separate thread with the subject Modbus Timeout error. Best regards |