2/23/2016 3:23 PM | |
Joined: 8/27/2014 Last visit: 9/9/2022 Posts: 10 Rating: (0) |
this is great.. it is working now. Thank you very much |
This contribution was helpful to2 thankful Users |
4/26/2017 2:18 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Hi Nohuman, 16#E7FE_0800 means timeout. Seems like your addressing of the module is wrong. Make sure you use the right HW-ID, LADDR and PORT at the IID_HW_CONNECT variable. Check out the documentation of this application example (chapter 3.3): Hope it helps. |
Last edited by: Owei at: 4/26/2017 2:21:39 PM |
|
5/2/2017 6:06 PM | |
Joined: 2/22/2016 Last visit: 9/25/2022 Posts: 9 Rating: (0) |
Hi Owei Please can you check my configuracion RFID? is it ok? AttachmentDoc1.docx (470 Downloads) |
5/11/2017 7:01 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Your addressing is correct. What's the order number of your reader? |