I have one s7 300 cpu , 10 IM 151 module and one hmi, all are in profinet network. i want to show each IM sf/bf led status on hmi. how to do this. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 10/2/2017 8:52:00 AMNew subject after splitting |
|
10/6/2017 1:14 PM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi, try this: PROFINET IO – Diagnostics Processing in the User Program hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |
10/6/2017 1:41 PM | |
Joined: 11/29/2011 Last visit: 9/26/2024 Posts: 1359 Rating: (232) |
Hi, I found this old example Getting the "Status for the CPU LED Indicators", that is point to start. See the Ladder programming examples (LAD). You can have a closer look at SFC51 if it not exactly what do you need. |
- What you read here, please check with manuals and your requirements. |
|
12/4/2017 10:51 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by klllll is split to a separate thread with the subject CM1241 RS422/485 and S7-1214 DC/DC/DC CPU: Want to show the transmit and receiver LED status of Modbus module on SCADA. Best regards |