8/18/2014 10:46 AM | |
Posts: 140 Rating: (7) |
Hello, After changing SFC's or CFC's have you updated the process cell in batch (BCC). |
4/9/2016 8:55 AM | |
Joined: 11/29/2011 Last visit: 5/7/2024 Posts: 1358 Rating: (231) |
Hi, It seems like in this case the Batch Control Server was configured to PC Based mode, and it lost com to the AS due to OS runtime was down. See the SIMATIC Process Control System PCS 7 SIMATIC BATCH V8.1 SP1 manual on page 47 for details. I hope I could help! |