Hi, First question: Are you going to use PCS7 software? You are going to need at least PCS7 V8.1 in order to operate the CPU410. The CPU410-5H is made exclusively for PCS7 using AS PO licenses as well as a SEC card on which PO are "installed" to determine the "power" of the CPU. See the following link for info about the controller. Link
|
If I could help you, you can use the RATE button. Thank you. |
|
5/26/2020 1:27 PM | |
Joined: 3/14/2008 Last visit: 11/14/2024 Posts: 2130 Rating: (953)
|
Hi, You can integrate your custom FB/DB/FC etc. in the PCS7 project. You can just compile and download the PLC using PCS7 functions. Make sure you follow the rules... FB range above 2500 is recommended for custom FB blocks. DB1 to 60 can be used for custom datablocks and FC60-700 can be used for custom FC's. You can increase the DB and FC range from the Compile settings in CFC if you need. I'm curious why you need to use the CPU410 if you aren't using PCS7.
|