3/10/2020 3:32 PM | |
Joined: 8/3/2009 Last visit: 11/12/2024 Posts: 14153 Rating: (1772) |
Hello Vishakha Yes this should work. I think the 1507S acts like a S71500 with internal interface like in the Communicatoin compendium: https://support.industry.siemens.com/cs/de/en/view/78028908 Page 73 Bye Murof |
If this Information really helps, you could use the Rate function |
|
3/11/2020 4:24 AM | |
Joined: 2/8/2018 Last visit: 3/28/2023 Posts: 256 Rating: (4) |
Hey , Thanks for the reply. But I got the answer through the manual that its no possible to communicate soft CPU 1507 with S7 300/400 . |
3/11/2020 9:02 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
okay, I just had a look into the manual, because I didn´t believe that. And there it is: SIMATIC S7-1500 Software Controller CPU 1505SP (F/T/TF), CPU 1507S (F), CPU 1508S (F) Version 20.8You can not communicate over S7-Communication. But there are much more possibilities to communicate. You con communicate over Open User Communication. Basic Examples for Open User Communication (OUC)hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |
9/1/2020 12:58 PM | |
Joined: 2/8/2018 Last visit: 3/28/2023 Posts: 256 Rating: (4) |
Yes I already mentioned that and about other types of communication, we know that we can do Open user communication but customer wanted to have clarity on S7 Communication so that was solved. |