10/4/2020 6:20 PM | |
Joined: 11/15/2019 Last visit: 9/26/2024 Posts: 63 Rating: (0) |
Hi there! I've been doing a few small projects lately and thanks to you guys everything has worked out so far . Now I have written a program for a filter installation, ... the program works fine, but unfortunately it looks super confusing because it contains A LOT of function blocks. My question is:is it possible to simplify this part of my program? This, so that it might save me time later with other programs and makes it easier to read for other programmers and myself. And of course this seems like a nice challenge to learn from! I have added a pdf of the program, I will explain furthe... on page 1 (the lower part) and two you can see a 'flushing cycle'. When 'manual flush' is pressed on the HMI OR when the pressure difference between the two pressure transmitters before and after the filters is greater than 0,5 bar It starts this cycle. In turn, a valve must be actuated for 5 seconds, then the valve must be closed / reset, after which there must be a pauze of ten minutes. This has to be repeaded for 12 valves. After the cycle it switches back to the normal program when the differential pressure has decreased or manual flush is ready (after four flushes on differential pressure, it generates an error message). as I said before it works perfectly now, but I would like to see it easier if at all possible. Love to hear from you guys! Kind regards, Robin Attachmentpdf.pdf (153 Downloads) |
10/4/2020 8:25 PM | |
Joined: 12/18/2014 Last visit: 9/26/2024 Posts: 33840 Rating: (4206)
|
I made you an example for 3 valves.
AttachmentValves_control_0BA8.Standard.zip (127 Downloads) |