5/23/2014 4:32 PM | |
Posts: 11 Rating:
|
hi Krriipc My huge doubt is here. as per the DSC_1782[1].jpg, i have connected Terminals 1 and 2 for '+' and '-' respectively. But I think what I have made is not in accordance to the manual on pg no 3 there is "Connection to a PLC/Recorder, separate supply". But if i make this as per "Connection to a PLC/Recorder, separate supply", The meter is not getting "ON". Also as per Pg no:22 in the attachment, the two wires should be directly connected from the transmitter to the module. I think a lot about "where is the current loop in this?". But dully followed as per the diagram in Pg no:22 Attachments7300_sm331_ai_8x12_bit_getting_started_en-US_en-US.pdf (552 Downloads) |
5/23/2014 5:17 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello kalidasan You need to check whether your transmitter is a 2-wire or 4-wire ? The Below attachement will help you understand the difference between the two. In both cases there are only 2 wires connected to the AI Module. In case of 2-wire ( Loop Powered ) the transmitter power is derived from the 4-20mA signal itself. In case of 4-wire, transmitter requires a separate auxiliary supply Hope this helps Cheers Navnag AttachmentDiff between 4-20ma 2Wire 4Wire.pdf (589 Downloads) |
There is no such thing as the last bug in a program |
|
This contribution was helpful to
1 thankful Users |
5/23/2014 5:45 PM | |
Posts: 11 Rating:
|
i'm using 2 wire 4-20ma. i'm damn sure about this. I'm not sure about this termination in the PLC side |
5/23/2014 5:49 PM | |
Posts: 784 Rating:
|
Attach screen shot for the connection into PLC
|
5/23/2014 6:02 PM | |
Posts: 11 Rating:
|
Hi Ayman Elotaify I get confused on seeing the module data manual only. Can you please say me how to make the termination i have attached my sensor manual with this. i want to know how to make the termination for Channel 0 in the AI module Attachment8750-1manual.pdf (556 Downloads) |
5/23/2014 6:27 PM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello kalidasan YourConnections on the PLC side are perfectly all right ( Hand sketch uploadedby you earlier ) Just for your ready reference, pl see attached the 2-wire wiring diagnam for 6ES7331-7KF02-0AB0 Hope this helps Cheers Navnag Attachment6ES7331-7KF02-0AB0_2W_4W.pdf (599 Downloads) |
There is no such thing as the last bug in a program |
|
5/23/2014 6:43 PM | |
Posts: 11 Rating:
|
Hi Navnag, Yes. I made as per your reference. But i think its not correct. |