4/5/2020 3:42 PM | |
Joined: 2/22/2008 Last visit: 8/6/2024 Posts: 2698 Rating: (207) |
Maybe the problem now is solved with minimum of changes, but you have to check this for all conditions. 1. The adding time is reduced to 0.2s, therefore we need a value of 3600*5=18,000 to increase the Wh counter. This value is high enough to add 10,000 W in any way, you never exceed the maximum of 32,767 of the arithmetic. If you have 17,999, you can add 32,767-17,999=14,768 W maximum. 2. The threshold trigger now has a time 06:98s, the low flow warning has a time of 06:00s. If it is possible, then increase the time to 7s or 8s. If this time is too large, then divide the gate time by 2 and double the constant V3 or halve the constant V4 of B004. You also can use any other gate time, but be careful for bad rounding in B004, otherwise you will lost accuracy. Good luck with testing, Scorp AttachmentTest3.zip (286 Downloads) |
4/5/2020 6:28 PM | |
Joined: 2/22/2008 Last visit: 8/6/2024 Posts: 2698 Rating: (207) |
Sorry for Siemens, but i have tried a simulation for an Eaton Easy E4 in ST (structured text). Just need a little time and get a solution with high accuracy. For me the program is better readable and also is very short. The advantage over the Logo is the 32 bit calculation without the internal rounding and more flexibility in structured text, if you use the right sequences. If the next Logo version in autumn don't have a much better firmware and software, then i know, what i will do in the future. Up to now i have only tested a few applications with the Easy E4 and i see more potential, 12 bit resolution for analog inputs, much more inputs and outputs possible, indexed addressing possible, structured text available and so on. If you are interested, see attachment. Regards, Scorp AttachmentEasy E4.zip (308 Downloads) |
4/5/2020 11:05 PM | |
Joined: 2/22/2008 Last visit: 8/6/2024 Posts: 2698 Rating: (207) |
If it is the impulse generator 0.2s, then we have a problem also with other times. But you can test the next version with time 1.0s and same trigger 18,000. Then you have n*5Wh in the first counter, that doesn't matter. Count up to 200 for 1kWh and multiply Wh with 5 for the display. The accuracy is not lost, only the last digit is rounded to 0 or 5. The problem also may be missing subtractions, overflows in the arithmetic or counter pulses are lost, but i see no problem in the moment. If the power display is okay, then there should be no decreasing of accuracy. How do you manipulate the program to get ~10,000 W without the sensor ? Regards, Scorp AttachmentTest4.zip (292 Downloads) |
Last edited by: Scorp at: 04/05/2020 23:08:11 |
|
Follow us on