10/1/2019 2:19 PM | |
Joined: 2/1/2010 Last visit: 6/4/2024 Posts: 146 Rating: (70) |
In CFC editor, you can change the selection of "Avoid implicit dead times" to be unchecked. Unchecking this puts it to "No correction" mode as seen in the help you attached. I believe the default is unchecked on a fresh installation, so maybe one of your colleagues changed it, or it was accidentally changed? |
If my post helped you, please rate. Thanks. |
|
10/1/2019 2:26 PM | |
Posts: 4 Rating: (1) |
Thanks for your answer, I also twas thinking about this option, but in my CFC this checkbox is missing (see attach). |
10/1/2019 3:01 PM | |
Joined: 2/1/2010 Last visit: 6/4/2024 Posts: 146 Rating: (70) |
Ah yes I see. I took the original screenshot from PCS7 9.0 SP2, my fault. I went back to a 9.0 SP1 VM and it also has the option, however that VM is fully patched. I found that this option was enabled in the ES Engineering Collection 9.0 SP2 for PCS7 9.0 SP1 in CFC 9.0 SP2 (up2) See attachment from CFC 9.0 SP2 Readme. You can find links to all the version patch pages from this excellent post: https://support.industry.siemens.com/tf/ww/en/posts/simatic-pcs-7-software-updates/189882/
|
If my post helped you, please rate. Thanks. |
|
This contribution was helpful to1 thankful Users |
10/1/2019 3:05 PM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (216) |
Hello Dmitry Kazantsev, the function to deactivate "Avoid implicit dead times" is only available with the CFC update. With regards |
This contribution was helpful to1 thankful Users |