2/12/2016 5:22 PM | |
Joined: 3/14/2008 Last visit: 9/27/2024 Posts: 2098 Rating: (938) |
Autoguy, Which PCS7 version do you use? At least in v8.1 when you change the name of a CFC chart, the runtime group is changed also the same. They have a relevant connection. The relevant connection is lost when you change only the runtime group name. Unless, you've created manual runtime groups, you have to manually change them. |
If I could help you, you can use the RATE button. Thank you. |
|
2/12/2016 6:13 PM | |
Joined: 3/14/2008 Last visit: 9/27/2024 Posts: 2098 Rating: (938) |
Auto Guy, I see what you mean. When there are more than two blocks in a chart, the runtime group name is not changed to the CFC chart when you rename the CFC... However the solution is this: - In CFC, go to Options->Customize->Copy/Move - Under: "Interconnection to runtime groups, When overwriting the chart" please select: "Remove" option P.S. You can change the runtime group names safely. However, like I said, the connection with CFC chart is lost, so the runtime group name is not updated anymore. In the old versions like v6.1, you had to create the runtime groups yourself. The program will be more efficient if you have multiple smaller runtime groups rather than one large runtime group. Processing is much faster. |
Last edited by: Oreca at: 2/12/2016 6:16:25 PMIf I could help you, you can use the RATE button. Thank you. |
|