9/9/2013 12:25 PM | |
Posts: 7 Rating: (0) |
HiKaulquappe!! first of all thanks for your answer!. I read the manuals and I tried to use BRCV but the CP441-2 is connected to a common datalogic barcode scanner that doesn't have the function of BSEND, it just send the data via RS232, 9600 baud, 8 bits, 1 stopp och none parity. CP doesn't report any error, actually the RTx lights on when i scan a barcode, i understand this as the CP is receiving data, but i cant read it via BRCV. I tried URCV as well, but it needs USEND And for the industrial ethernet option i have an anybus converter RS232 to Profinet and a siemens switch. To the CP343 is connected a WinCC PC, so i was thinking to connect the winCC PC, the anybus converter and the CP343-1 to the switch. Hope you can help me, i am a bit lost here. Best Regards!
|
9/11/2013 9:53 AM | |
Posts: 7 Rating: (0) |
HiKaulquappe!! It worked!!!.........It worked with a new connection as unspecified and BRCV calling to the connection address (1002 HEX). Then i proved without a new connection but calling direct to the Input address of the CP in HW (8180 dec, 1FF4 HEX). and it also worked!. Anyways i used a new connection to be safe because according to the description tha ID of BRCV is between 1000 HEX and 1400 HEX. Thank you very much for your help and patience!!
|
This contribution was helpful to2 thankful Users |