4/25/2025 12:56 PM | |
Joined: 4/11/2022 Last visit: 9/14/2025 Posts: 90 Rating:
|
you forgot to attach the projetc. |
Rgds, |
|
4/25/2025 1:20 PM | |
Joined: 3/27/2024 Last visit: 6/14/2025 Posts: 11 Rating:
|
Sorry I am old , and new with the forum
Attachmentattachement.zip (189 Downloads) |
4/25/2025 7:34 PM | |
Joined: 3/27/2024 Last visit: 6/14/2025 Posts: 11 Rating:
|
My Logo : 6ED1052-1CC08-OBA2 with analog output module and modbus TCP with USR-TCP232-410s |
4/25/2025 7:36 PM | |
Joined: 3/27/2024 Last visit: 6/14/2025 Posts: 11 Rating:
|
manual USR232TCP232-410s
AttachmentUSR-TCP232-410S_User_Manual_V1.0.0.pdf (349 Downloads) |
4/26/2025 8:23 AM | |
Joined: 3/27/2024 Last visit: 6/14/2025 Posts: 11 Rating:
|
the settings for the test are OK : unit ID 43 and startadres for L1 ( 19 ( 18 + 1 for PLC ) You can see that on the website of smartstuff https://docs.smart-stuff.nl/p1-modbus-dongle/quick-start/registers The result is 100 % ok in the test file that is attached . the problem is there when I try with the registers "delivred power ) adres 14 and returned power , adres 15 ( see word file in my first mail ) and the reason is that it is given in kWatt and I need it in Watt . So when it is less than 1 kW , the result is 0 Attachmentattachement.zip (203 Downloads) |
Follow us on