12/9/2011 3:26 PM | |
Joined: 10/26/2011 Last visit: 5/14/2024 Posts: 761 Rating: (190) |
Product PCS7 OS Operator Station Version V7.1 SP1 How do you specify the text for the OpDi03 faceplate? Solution Please find attached document. The OpDi03 faceplate text can be significantly customized; however, not all of the values are obvious on where to set the text. Current Status and Current Command Text The current status text is set by opening the Object Properties of the “FBK#IN” inputs on the instance of the block and setting the text for the Value property. The current command text is set by opening the Object Properties of the “OUT#” outputs on the instance of the block and setting the text for the Value property. Operator Command Button Text The text for the operator command button is defined by opening the Properties of the Block Instance in CFC editor, selecting the I/O’s tab and entering text in the Text1 column for SETOP#. AttachmentEngineering_Steps.pdf (87 Downloads) |
SIMATIC PCS 7 - Overview |
|
This contribution was helpful to1 thankful Users |