3/28/2020 7:47 PM | |
Joined: 9/8/2019 Last visit: 12/16/2021 Posts: 54 Rating: (0) |
the used logo is logo!230RCE>... the number of signals needed to be collected is 42 from 42 logo remotely |
3/28/2020 7:49 PM | |
Joined: 9/8/2019 Last visit: 12/16/2021 Posts: 54 Rating: (0) |
the signals are analog bus after normalizing and scaling,, which means they are may be considered digital |
3/28/2020 7:50 PM | |
Joined: 12/18/2014 Last visit: 5/17/2024 Posts: 33052 Rating: (4082)
|
A LOGO! can communicate at maximum with 16 other LOGO!s. |
3/28/2020 8:12 PM | |
Joined: 9/8/2019 Last visit: 12/16/2021 Posts: 54 Rating: (0) |
yes that is it 42 signals from 42 logos each signal is analog! apologize if I did not make my self clear! |
3/28/2020 8:20 PM | |
Joined: 12/18/2014 Last visit: 5/17/2024 Posts: 33052 Rating: (4082)
|
I don't know if it's possible to make a network projekt with 42 LOGO!s. I can make you an example 8 LOGO!s and a collector LOGO!. If you want to know if it is possible with 42 LOGO!s then start a Support Request. Then became you an answer form Siemens directly.... |
3/28/2020 8:26 PM | |
Joined: 9/8/2019 Last visit: 12/16/2021 Posts: 54 Rating: (0) |
thank you very much :) ! I want to use DNS ?? can I?? |
4/2/2020 6:57 AM | |
Joined: 9/11/2014 Last visit: 5/17/2024 Posts: 722 Rating: (28) |
Hi, DDNS is not supported for your appliacation. Each LOGO! must have a individual IP-Adress. |
8/7/2020 9:26 AM | |
Posts: 1 Rating: (0) |
LOGO can communicate maximum 16. |