8/3/2018 9:26 PM | |
Joined: 11/15/2017 Last visit: 12/1/2022 Posts: 23 Rating: (0) |
Sir, Does this block supports 6 digits register address like I want read 421300 register in energy meter but I am getting the error as start or end address over range status value e002h.Kindly please help for the same. Thanks in advance. Regards, Raj |
This contribution was helpful to1 thankful Users |
8/8/2018 3:26 PM | |
Joined: 12/1/2009 Last visit: 10/27/2024 Posts: 672 Rating: (147) |
Sorry my friend but I don't visit the forum on regular basis. Anyhow, kindly find attached MBMAREQ block for 6 digit registers. Also one confusion I have. Plc can read address up to 65535. So how it can read any 6 digit address? That's quite simple, just the old fashion way. You must provide the function code by yourself. Good Luck. AttachmentMBMAREQH.zip (862 Downloads) |
Give us your feedback and show us your respect! |
|
This contribution was helpful to5 thankful Users |