Hi STB601, Which module are you using for that address range. I think the configured module is not supported by PCS7-> Like a ET200M module or AI card. The module driver cannot be linked because the module is unknown. When you open hardware configuration, you have your catalog on your right. It should say: "PCS7_Vxx" profile. This allow you to configure only released modules for PCS7. When you set this on "Standard", you will see a lot more modules. Please check the following manual to check if the configured module is released. |
Last edited by: Oreca at: 5/26/2016 9:09:24 AMIf I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to1 thankful Users |
5/26/2016 3:58 PM | |
Joined: 3/14/2008 Last visit: 5/14/2024 Posts: 2066 Rating: (928)
|
Hey STB601, Thx for the feedback and good that you found the solution. What I wanted to say further... I recommend you use IW and QW. You can configure the input and output cards then in the PIP,which is the process image partition and this means that inputs and outputs are set active during an OB interrupt cycle, which is different from OB1. It also improves accessing speed. I dont know if you want more info on the PIP, but using PIP in interrupt OB's is highly recommended rather than the use of OB |
If I could help you, you can use the RATE button. Thank you. |
|