3/25/2010 10:48 AM | |
Posts: 38 Rating: (2) |
The project configuration is one ES/OS and one OS. Both ES/OS and OS are single stations. ES/OS is configured as WinCC Application and OS is configured as WinCC Appl Ref. The first download is without any problem. WinCC could be activated in runtime without any problem. After deactivating the WinCC in OS, when the entire WinCC project down load is tried we get an error message. But no specific error. Now if we open WinCC in OS we get a message "configured server not available" and we could not activate the runtime also. If we delete the OS folder and download again, no problem with first download and second download we face the same problem. Download of entire WinCC project may be required if delta or online download gives any error and we cannot download without deleting the OS folder. If we delete the OS folder, we may loose all the logging. Why we could not download the entire project 2nd time or later? Any specific settings to be done to avoid this problem. I would be thankful for the solution to this problem as we have to start the commissioing shortly. Regards, Krishnan AttachmentDownload OS.zip (512 Downloads) |
3/25/2010 3:07 PM | |
Posts: 38 Rating: (2) |
Windows firewall is not on. Windows firewall is turned off in both ES/OS and OS. |
3/26/2010 12:16 PM | |
Posts: 55 Rating: (4) |
In my case, it happens when you do a direct download also! |