11/29/2018 4:12 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Ok, so for a S7-1500 and a RF380R I'd suggest to use the PROFINET communication module RF180C (see attached screenshot) since you just can't connect the reader directly to the PLC. You will only have to configure the PLC and communication module in TIA Portal. Just plug reader into the module. To control the reader I suggest to use the "Ident blocks". Here's an example on how to use the blocks: |
11/29/2018 4:47 PM | |
Posts: 23 Rating: (0) |
I've check with the colleagues the plc model and is a 1215C DC/DC/DC (6ES7 215-1AG40-0XB0) And with the plc i have a RF380R (6GT2801-3AB10) and (but im not sure at this point) a RF340T. |
11/29/2018 5:04 PM | |
Joined: 10/1/2013 Last visit: 5/8/2024 Posts: 605 Rating: (71)
|
Ok, with S7-12xx you'll need the RF120C communication module. And here is the how-to example: The transponder doesn't matter. Which ever RF3xxT it is, it'll work. |
Last edited by: Owei at: 11/29/2018 5:05:24 PM |
|
11/29/2018 5:25 PM | |
Posts: 23 Rating: (0) |
And where i can find the RF120C gsd ? Or I don't need it ? |