Hello Zoom; Please take a few seconds to provide this additional information: 1.- what state are the diagnostic LEDs n the CPU (Profibus master) and on each of the repeaters (identify them as R1, R2 and R3 on your drawing); What do the LEDs indicate on the standard repeater? https://support.industry.siemens.com/cs/fr/en/view/103709539 2 - Are the Profibus connection wires (Red and Green) systematically connected to all repeaters (and on the slaves): - Green to A1/A2; - Red to B1/B2; 3 - if there is a SF/BF LEd active in the CPU, what are the contents of the diagnostic buffer? Also, you could try disconnecting R2 and R3 from the network, leaving only the CPU and R1, with its connected slaves.; see if you can activate R1 and read the slaves in the Profibus master.That would limit the possibilities of error in your setup, and simplify the diagnosis. Hope this helps, Daniel Charter |