2/28/2012 2:43 PM | |
Posts: 6 Rating: (0) |
Can you ping the ip address of the PLC ? I believe the default is 192.168.0.1 |
2/28/2012 2:53 PM | |
Joined: 8/16/2010 Last visit: 11/5/2024 Posts: 638 Rating: (12) |
I try to ping but it not works. Maybe the CPU is broken? |
2/28/2012 3:50 PM | |
Posts: 6 Rating: (0) |
Did you change the IP address on the laptop/pc port to match the same subnet ? Try changing the IP on your pc to 192.168.0.200, then try to ping again. |
2/28/2012 3:51 PM | |
Joined: 8/16/2010 Last visit: 11/5/2024 Posts: 638 Rating: (12) |
Thanks, I also try that but it didnt work :( |
2/28/2012 4:28 PM | |
Joined: 7/7/2010 Last visit: 11/14/2024 Posts: 15399 Rating: (2443) |
Have you tried the PST? It should find the PLC/CPU and allow you to set the IP address. Just power cycle the PLC, and use the Primary Setup Tool ( https://support.automation.siemens.com/US/llisapi.dll?func=cslib.csinfo&lang=en&objid=20414744&caller=view) After that, you can do a PLC reset to factory defaults (with the ip still set). Once you can successfully ping the PLC, you should be able to download a project and get it to start into run mode. |
science guy |
|
2/28/2012 4:39 PM | |
Joined: 9/23/2005 Last visit: 11/14/2024 Posts: 4352 Rating: (1452)
|
Hi, check if the tips in Tips: S7-1200 / STEP 7 Basic - Check list for first online access /tf/WW/en/Posts/46536#top are usefull. Else, I suggest you update the CPU FW. If it doesn't work, maybe should be a case of fault... |
Denilson Pegaia |
|
2/29/2012 2:25 PM | |
Joined: 8/16/2010 Last visit: 11/5/2024 Posts: 638 Rating: (12) |
Thanks all... I will try your solutions... Thats is new PLC, not configured before. I will inform you whats heppend. |