3/4/2008 11:49 AM | |
Posts: 5822 Rating: (412) |
Dear gama, well... as the information I receive from you continuously changes I draw a scheme what I think you have till now. If you have changes please change it the way you have it. So, referring your questions I can tell you that depending how the configuration looks like, if the ?? is Ethernet and the local PC (Server??) is also connected to this Ethernet both PCs can access the Master PLC via Ethernet. Win CC can read and write values in the Master PLC... but this is the End. The PCs are not able to access the other Slave PLCs, because the Modbus interface does not allow this. The Slave PLCs can communicate with the Master and the Master may provide this Information to the PCs, but a direct communication between the PCs and the Slaves will not be possible. Even Communication between the Slaves will only work over theprogram on the Master... so think about it. As an alternative I would choose IWLAN, there you can access the complete Network and each node is able to communicate with another. Best regards J_Bell AttachmentConfiguration.zip (202 Downloads) |
3/5/2008 9:05 AM | |
Posts: 15 Rating: (0) |
Dear J_Bell Sorry for the mess up. I have changed the configuration according to the plan. I hop the modbu part works, though i am not quite sure. First Q : Does the network work with RS232 Modbus or must be changed to RS485 modbus modules? Second Q : I think there are two ways to communicate with a remote station, shown with 1 and 2 in red color, so the red dotted lines are the 2nd question, which one is practical and is there any other ways? What devices (HW or SW) are needed? I thank you so so much to keep in touch AttachmentMy Configuration.zip (172 Downloads) |