Hello, in picture of your
first post it seems that there are also other errors/alarms present besides
F01912. If the telegram is
choosen inside drive configuration, the interconnections are done in drive
automatically. The sign-of-kife tolerance (p925) is just preventing sporadically occuring failures
in sign of life. To check controller
sign of life you can trace automatically generated PLC tag of technology object
for that axis. A telegram overview
you can get at list maual of S120 (chap. 3.9, starting at plan 2415 ff.) |