Hi, with the motion technology objects you always need to check which parameter can be changed in which way! This is described for each TO and each parameter in the corresponding manual, for TO OutputCam this is here: https://support.industry.siemens.com/cs/ww/en/view/109812060/121798671243 Legend for column W which you need to check is here: https://support.industry.siemens.com/cs/ww/en/view/109812060/126734652683 So for what you are planning to do, you cannot write this parameter with a simple assignment, but need to use WRIT_DBL to change the value in the load memory, then do a TO restart with MC_Reset instruction (and using its input Restart=TRUE) to make the changes effective. And of course you also would need to ensure that all the necessary parameters for this other cam type are also all valid. If this is suitable depends only on your application. Restarting the TO takes a moment, during which it does not do its work (as it is restarting). You might consider 0_EInstein's suggestion with using two TO OutputCam and just switching between the two. Regards, |