3/29/2024 8:19 AM | |
Joined: 3/30/2020 Last visit: 7/12/2024 Posts: 4624 Rating: (967) |
Hello. Welcome.
What you wish to do is possible. The instruction you use to invoke the execution of the command table gives the ability to start at any step you wish. You can have several sequences within one table but you could also have several tables. More than this: It is possible to have the user program edit the entries in the table. The motion command table is a very powerful tool. Interesting enough only the S7-1200 makes this available. But I will confess that we use the motion control instructions instead of the table to control the motions of our machines. Some reference materials: S7-1200: Faceplate for Editing the "Command Table" As last note: Be careful in your consideration if you are using absolute or relative motion. Each has its good side and bad side so there is not a wrong choice. But you need to consider scenarios like recovering from an interrupted run. |
3/29/2024 2:48 PM | |
Joined: 12/23/2023 Last visit: 5/28/2024 Posts: 3 Rating: (0) |
Yes so far so clear but if i revoke the execution it won't start a second time because the DB has Done as a True Value. |
