Joined: 9/7/2023 Last visit: 5/19/2024 Posts: 2 Rating: (0) |
Dear All, I am writing to seek your expertise regarding the problem I am facing with our Simovert MasterDrive MC. We have Siemens PLC S7-300 CPU (315/2DP). Connected with MasterDrive MC System to Position Step in the Machine Drive Part No. 6SE7021-0EP70-Z (Z= G91+C43+K80) We encountered an issue with our device, prompting us to procure a replacement from a local supplier. We ensured to retain the parameters of the original device for a seamless transition. We received the replacement device, identical in part number. However, upon attempting to download the original device parameters, we were presented with the following: that the Original MasterDrive MC unit version is: 2.4 and the new MasterDrive MC unit Version: 1.6 and the drive did not work. Is there any way to update the firmware regarding to the attached Details. AttachmentMasterDrive MC Version Issue.zip (392 Downloads) |
Last edited by: Jen_Moderator at: 05/17/2024 05:25:39Text formatting optimized. |
|
5/17/2024 7:17 AM | |
Joined: 10/11/2006 Last visit: 10/17/2024 Posts: 5923 Rating: (810)
|
Dear mahmoud_shaban_ahmed, no, there is no way to update a MD device from 1.6 to 2.x. FW v2.x indicates a MD device with Performance 2. This was a "new" Hardware platform for Masterdrives. FW 1.x indicates the old Hardware platform for Masterdrives MC. Please find a little Guidline under the following link: https://support.industry.siemens.com/cs/de/en/view/16704599 In the order number it is indicated like the following example: |
Last edited by: Jen_Moderator at: 05/17/2024 10:25:07Link optimized. With best regards, |
|
This contribution was helpful to1 thankful Users |