8/5/2006 4:12 PM | |
Posts: 39 Rating: (0) |
Dear Late, Thanks again four your attention. i send you my configuration . In HW-Config the I/O modules are shown by (X) . and in online mode by diagnostic the module i have different error formost DIs and all DOs. for DI the error was : cyclic Reduncancy Check (CRC) error in data message frame for DO the error was : incorrect parameter assign The SF LED for all IMs and all DOs are on,but 2 of DI modules are OK and others have this fault. !!!!!!!! Best Regard Attachmentplc13.zip (867 Downloads) |
8/8/2006 4:42 PM | |
Dear Late I'm so confused in working with F-I/O. I checked every thing and still have problem. Iremove all myCFC chart from the CPU and add only one channel for each DI and DO module for automatic module drive creationwhile compiling. when i RUN cpu for 6-7 sec all thing is OK but after that all SF LED in modules are ON. i send you my chenged configuration and diagnostic of CPU, DI and DO in online mode. what should i do? Thanks again for your significant help. AttachmentDiagnose 2.zip (797 Downloads) |
