Hey elctro hamad, which Kind of WinCC Runtime dou you use? WinCC RT Profesional? In a faceplate you can't write HMI tags outside the faceplate. You have to define tags inside the faceplate. You can write values through the properties with "\properties\#propertiename#"
https://support.industry.siemens.com/cs/ww/en/view/85239213 With best regards cumulus |
Last edited by: cumulus at: 12/18/2017 2:52:22 PMLearn more about visualization - visit the HMI courses of Siemens AG! |
|
12/19/2017 11:30 AM | |
Joined: 5/8/2016 Last visit: 2/15/2024 Posts: 167 Rating: (13) |
Dear cumulus thanks for help i succeeded to solve the issue with VB script as shown in the picture attached |
A lot of potential remains |
|
This contribution was helpful to1 thankful Users |