2/28/2023 4:02 PM | |
Joined: 10/11/2006 Last visit: 10/17/2024 Posts: 5923 Rating: (810)
|
Dear abbasisahab, After default settings, the drive waits for the setting of the motor data thats °005. The "?" in the DriveMonitor window means that the USS baud rate doesn't fit. The link to the compendium Masterdrives MC1.6:http://support.automation.siemens.com/WW/view/en/23660019 The link to the DriveMonitor tool:http://support.automation.siemens.com/WW/view/en/11769381 |
With best regards, |
|