Hello Everyone, I need to give the input in S5 Timer in Simatic Manager S7-317 from SCADA but In SCADA its a real but i am not able to real tag onto S5 Timer input and the timer did not work. So Please help me to do any conversion or how can I run that timer with real input? ------------------------------------------------------------------------------------------ |
Last edited by: The Helping Hand at: 03/14/2024 14:22:56New subject after splitting |
|
3/14/2024 2:39 PM | |
Joined: 7/9/2015 Last visit: 8/30/2024 Posts: 3943 Rating: (585)
|
Hi, You can use FC40 / TIM_S5TI from Step 7 standard library - for more Informations please check chapter Converting the data types INT (INTEGER) and REAL into data type S5TIME in the following FAQ: How can you convert a number value of the data type INT into a string in S5TIME, or into the data types BCD and REAL?Regards, Towome |
|
|