Hello, I will assume that you are talking about F-DI24 , ET200M Module "6ES7326-1BK02-0AB0". First download Automation System S7-300 ET 200M Distributed I/O Device Fail-safe signal modules and see section 8.3.2. *attached Go through the flow chart to know which application match your needs. Then adjust in setting the behavior at discrpency. It can be And, Or, last valid value,.. And also time of discripency between 10ms to 30000 ms. |