Hello, (1st sorry for my english) I experimented several problems using that awfull TIA ADMIN. I spent many hours to manage to make it work so i hope this topic may help other. My System :
When I tried to use it this error happened : This page can't be reached localhost refuses to connect. Try the following: Check connection Check the proxy and firewall ERR_CONNECTION_REFUSED What you need to check :
Wrong or old thing to check :
Last thing : The login and password requested is your windows session login, not the siemens one. (that's really stupid i knnow...) (feel free to add informations since "official way" is silent for years now) Good luck! |
Last edited by: D. Fort at: 10/29/2024 17:09:58Last edited by: D. Fort at: 10/30/2024 08:01:27Last edited by: Moderator_Lan at: 10/30/2024 08:43:59links optimized |
|
This contribution was helpful to3 thankful Users |
11/1/2024 7:09 PM | |
Joined: 10/30/2024 Last visit: 11/12/2024 Posts: 1 Rating: (0) |
This WMIC solved it. A Windows update must have decided to turn this option off. Thank you, sir.
|
11/5/2024 11:16 AM | |
Joined: 3/14/2017 Last visit: 11/12/2024 Posts: 9 Rating: (0) |
The installation of WMIC solve it. Thank You Mr D.Fort Link for WMIC install guide: |