Hi. To reach PLd two contactors and evaluation of the feedback channel are mandatory. (see attached picture) For more information please have a look at the Application Manual "SIRIUS Safety Integrated" (page 41) https://support.industry.siemens.com/cs/ww/en/view/81366718. Best regards! |