Hello I Hope you can help me. I am attempting to configure a profibus network on a TI-555 PLC with Com Profibus. When Selecting a Module type on my 153-2BA01, 1 have 2 modules that match myu part number. 6ES7 322-1BH0*-0AA0 (16DO) and 6ES7 322-1BH*1-0AA0 (16DO). Both match 6ES7 322-1BH01-0AA0 so which one should be used? Thank You! Alan Splitted from GSD FILE FOR 6ES7153-2BA01-0XB0. |
Last edited by: O_Moderator at: 6/3/2011 1:01 PMnew subject after splitting |
|
6/3/2011 6:01 AM | |
Joined: 8/25/2006 Last visit: 10/18/2024 Posts: 2209 Rating: (279) |
Hello. Are you sure you select right slave from catalog while inserting it into configuration. IM153-2 with order number 6ES7 153-2BA*1-0XB0 have gsd-file si03801e.gse (look at screenshot Si03801e.jpg). And this slave have only 6ES7 322-1BH01-0AA0. I think you have inserted another slave - IM153-1 6ES7 153-1AA**-0XB0, which have gsd-file SIEM801D.GSE(look at screenshot Siem801D.jpg), and it really have 6ES7 322-1BH0*-0AA0 (16DO) and 6ES7 322-1BH*1-0AA0 (16DO). Attachmentscreen.zip (537 Downloads) |