Posts: 2964 Rating: (484) |
Hello.... You can see this error infromation in Docon WEB link attached.... https://www.automation.siemens.com/doconweb/content.asp?item=12771&cd=sinumerik_simodrive_04_2010_e&scope=all also you can see in SIMOCOMU too... Error 514 means "Zero mark monitoring, direct measuring system" Cause=>A fluctuation in the measured values has occurred between 2 encoder zero marks (encoder pulses may have been lost). Note:The encoder monitoring can be disabled using P1600.14.Remedy – Use the original Siemens pre–assembled encoder cables (better screening) – Check for sporadic interruptions (loose contact, e.g. due to cable drag movements) – For toothed–wheel encoders, check the clearance between the toothed wheel and sensor – Check the encoder, encoder cables and connectors between the motor and control module – Check the shield contact, front panel, control module (upper screw) – Replace the encoder cables or the control module – Replace encoder
|