1/4/2010 3:27 PM | |
Posts: 661 Rating: (123) |
Also to you a happy new year there are4 possibilties: 1) via LOGO! menu / TD menu: Go to "set param", choose the block number of the pi-controller and press OK. Then you can change the setpoint. 2) Display the SP parameter in a message text. Then you can change the SP by pressing ESC for 1 second. 3) With the F-keys of LOGO TD. Please look here: http://support.automation.siemens.com/WW/view/en/34914500 4) With a potentiometer (or other analog values): http://support.automation.siemens.com/WW/view/en/24002694 |
This contribution was helpful to1 thankful Users |