5/18/2011 12:53 PM | |
Posts: 7 Rating: (0) |
Hi, I have S7-300 315-2DP (6ES7 315-2AG10-0AB0 V2.6) Processor which configured asDPslave port the has been configured. From the master ABB (DCS) the node of my plc is able to view but not able to transfer data, i dont the whether the GSD file which has been confirgured is correct. Can i have the latest GSD and the error sheet has been attached. Thanks & Regards S.Veera AttachmentReport.pdf (110 Downloads) |
5/21/2011 9:42 AM | |
Posts: 947 Rating: (45) |
1. Aret rightly said - in HW-config should not be slave 2. CPU 315 should be configure - see attach. 3. ABB should configure. 4. input byte for ABB is output byte for Siemens CPU. output byte for Siemens CPU is input byte for ABB 5. Check Slot numbers when configuring Attachmentconfig_cpu.ZIP (105 Downloads) |