Hello aclsy yes, you can (well, should be able to) operatethe ET200M with redundant IM's on an ABB system, but there's a few things to look out forand the FAQ below contains all the details: How do you operate an ET 200M IM 153-2BAx1/-2BAx2 on a redundant ABB system, the AC800M?(PM 864A controller with DP master CI 854A) I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
2/21/2012 8:35 AM | |
Joined: 10/7/2005 Last visit: 10/17/2024 Posts: 3024 Rating: (1054)
|
Hello aclsy I fear there's some confusion going on here. I was under the impression you want to use ET200M's I/O stationsas (redundant) DP slaves of your ABB system. It seems though that you have ET200M I/O'stations as (redundant) DP slavesof an S7-400 H system and now want to create a Profibus linkfrom the S7-400 H system to the redundant DP Master interface of your ABB sytem, correct?. If so, usage of DP/DP couplers would possibly the easiest way to do so (and no, you can NOT use an IM152 DP Slave I/O station as a DP Master). If you are unfamiliar with DP/DP couplers, downloadthe manual from HERE and note that you'll also find plenty of additional info (FAQ,s Forum posts etc.) for them with a search@ https://support.automation.siemens.com P.S: Dont know if a redundant DP Slave interface is avialable for your ABB system, perhaps other may know, if notI suggest you contact ABB (should it exist, you should be ableto make the ABB system a redundant DP Slave of your S7-400 H system) |
Cheers |
|
This contribution was helpful to1 thankful Users |