Hello, Please check values in r947 & r949 indices, i.e. r947 stores fault message & r949 fault value. Value stored in r949 is helpful to find out cause of fault which is described in chapter "Faults & Alarms" in manual. |
Last edited by: Jen_Moderator at: 06/28/2021 09:51:34Optimized link. |
|
This contribution was helpful to1 thankful Users |
6/27/2021 1:46 PM | |
Joined: 3/26/2016 Last visit: 9/20/2024 Posts: 31 Rating: (0) |
I understand, but when i'm turning on the machine to function the motor - i hear the relay shift over and the motor gets power. When i'm doing P115-2 - i take control from the drive and turn the drive on then I get error F002, I think i am missing a step for turning the drives on. 1. Set P115-2 2. Take control of drive and turn drive On - do not see motor kick on 3. Am I missing a step somewhere to see the motor kick on? |
6/15/2023 1:56 AM | |
Joined: 4/27/2023 Last visit: 2/19/2024 Posts: 7 Rating: (0) |
Hello,this is happening to me too.i cant make p115=1 what should i do? thank you |