4/1/2025 10:23 AM | |
Joined: 11/4/2020 Last visit: 4/7/2025 Posts: 3 Rating:
|
Hi All, Or is this just not possible with this level of hardware ? |
4/1/2025 10:34 AM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35070 Rating:
|
Is the LOGO! also a LOGO! 8.4? Yes, it's possible. Example: 1. Alarm = V101.0 In the alarm table use then VW100. |
Last edited by: ixo65 at: 04/01/2025 10:35:27 |
|
4/1/2025 1:07 PM | |
Joined: 11/4/2020 Last visit: 4/7/2025 Posts: 3 Rating:
|
Fantastic, so it can be done. Thank you for your reply Yes it is a Logo! 8.4 So in the VM configuration I can't see my fault relay coil M32 for example to map it to VW100 Is there another block I need to use rather than a standard relay coil so it appears in the drop down of VM configuration window ? Or is there another way to do it ? |
4/1/2025 1:18 PM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35070 Rating:
|
You don't need the VM parameter assignment. The V-bits V100.0 to V101.7 are part of the word VW100. And you can assign the M32 to the V-bit via the digital network output. |
This contribution was helpful to
1 thankful Users |
4/1/2025 3:54 PM | |
Joined: 11/4/2020 Last visit: 4/7/2025 Posts: 3 Rating:
|
Perfect, Thank you for your assistance. That sorted it |
This contribution was helpful to
1 thankful Users |
4/1/2025 3:57 PM | |
Joined: 12/18/2014 Last visit: 4/9/2025 Posts: 35070 Rating:
|
That's sounds good ... |