9/27/2010 1:59 PM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hello, Try to import in COMPROFIBUS this GSD GSD_Profibus_DCM. Best regards, Hristo Mihalev |
9/27/2010 3:01 PM | |
Joined: 10/7/2005 Last visit: 10/19/2024 Posts: 3024 Rating: (1054) |
Hello NPSK having the correct GSD file is a good start, but please check the communication in you S5 program too. 6RA24's with a CB24 (or their successor the 6RA70's with a CBP for that matter) had the so called PKW's which is a 4 Word long area in the PPO type (Process Parameter Obeject) and allowed for freely configurable Parameter reads and/or writes. 6RA80 (or mostother Sinamics for that matter) do NOT have this 4 Word long PKW area anymore in their Profibus comms structure. IF your S5 program used the PKW area to read (or write) Parameters from the 6RA24 you will have to find a different way to implement this with 6RA80's (e.g. use PZD's, change Parameter sets etc.). It may not be applicable in your case (i.e. PKW's are not used) but you ought to be aware of this and I hope this helps. EDIT: Siemens has started to re-introduce the "missing" PKW area into Sinamics again with newer firmware versions, G120's with SW3.0 for example make thePKWarea available again (see HERE). Perhaps 6RA80 will one day have the PKW's area again too. |
Last edited by: fritz at: 10/5/2010 2:12 AMCheers |
|
This contribution was helpful to3 thankful Users |