5/22/2014 6:28 PM | |
Joined: 3/15/2011 Last visit: 9/18/2024 Posts: 134 Rating: (9) |
Dear Experts, I want to operate SINAMICS V90 drive(6SL3210‐5FE10‐8UA0) on dc supply but for the protection confusing for selection of fuses??? Hi, SINAMICS V90 INPUT: 3AC 380-480V -15%/+10% 2.6A 45-66HZ OUTPUT: 0-INPUT V 2.1A 0-330HZ PROTECTION: IP20 MOTOR:0.75KW . this drive model works on 3AC as mentioned in the catalog ,i wonder how can you give DC Supply to it (600 VDC). As far as fuse selection is concerned you can go with corresponging range of sinamics Drive. please refer attachment Hope this helps regards Ashutosh Attachmentfuse_sinamics.pdf (361 Downloads) |
This contribution was helpful to1 thankful Users |
5/24/2014 11:48 AM |
|
Posts: 235 Rating: (52) |
Dear Chetan2490 As you said that if V90Drive working on Dc supply than Pls find the attached shhet to selection of semiconductor fuse as per ampere rating. hope this will help yo select the fuse for the same Attachment3NE DC fuse.pdf (309 Downloads) |
Follow us on