8/28/2025 7:34 AM | |
Joined: 3/14/2008 Last visit: 9/4/2025 Posts: 2216 Rating:
Hi, The Chart-in-chart block cannot be set to a runtime group. The runtime editor assigns the blocks inside the chart in chart just like the other blocks in the parent CFC. You can set however a predecessor when right clicking a block and select: "Predecessor for Insertion Position". If you do this inside the chart-in-chart, the next block inserted in the parent CFC, will be placed behind the block in the chart-in-chart. You can also open the runtime editor and right click on the CFC and select: "Optimize Groups/Tasks". Then the whole chart will be assigned automatically in the correct order based on interconnections. |
9/1/2025 9:00 AM | |
Joined: 12/2/2016 Last visit: 9/1/2025 Posts: 89 Rating:
I have find a method by myself when On OFFLINE MODE just by drag the runtime sequence like the following picture |
9/1/2025 9:09 AM | |
Hi, When you change the runtime sequence, you change the program. Therefore, you need to download change the CPU. |