8/2/2019 8:10 AM | |
Posts: 31 Rating:
Hi, how will work master slave DC drive 6RA70 with PLC S7-300. Pl. explain in how logic has to be written. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 08/02/2019 11:33:00New subject after splitting |
8/2/2019 9:26 AM | |
Posts: 31 Rating:
Hi, Master D.C Motor is connected with analog tacho. |
8/3/2019 6:30 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating:
Hello, There is no ready application example. Have you seleceted CPU? In PLC hardware project you need to install Master drive & I guess you want to establish connection over profibus. If yes you need to install PROFIBUS board CBP2. Please refer manual SIMOREG DC-MASTER 6RA70; software version 3.1 chapter 7.7.2 page no 180. Select appropriate PPO type. Tune/optimise the drive as per stand alone unit & then establsih communication with PLC. HTH. |